This week, the EIA was updated to include the TRC (Technical Review Committee) Comments and Proponent Response Report. In other words, the government's questions for Voltagrid/Beacon and their answers. It is not a light read by any stretch (if you are interested in birds, there are pages and pages of questions about them), but there are a few interesting responses in there. Also, plenty of 'we will get back to you on that' responses.
https://www.gnb.ca/content/dam/GNB3/t/en...s-enregistrements/1657-/1663-round-1.pdf
Quote:
TRC COMMENT:
Has the proponent considered the following alternatives to 50 x 4.5 MWe natural gas fired combustion turbines?
1. One or more, more appropriately sized natural gas combined cycle turbine generating units?
2. Solar PV and Battery Energy Storage System?
3. Contracting with a renewable developer connected elsewhere on the electricity transmission system, with Battery Energy Storage System's located on premises?
For each of the three alternatives, please explain why they were not considered, or if they were please elaborate as to why they were not selected as the proposed option.
|
Quote:
PROPONENT RESPONSE:
The proponent has considered the identified alternatives. A hyperscale datacenter has very specific reliability requirements (99.9% reliability), 100% IT instantaneous load (on and off on a 200 MW scale), and variable loads in millisecond increments. Combined cycle turbines can only increase at a rate of 1% per minute (making them unsuitable for 100% IT instantaneous load) and variable power loads also mean worse fuel usage and emissions as well as turndown problems on the combined cycle component (meaning that the plant would not be able to operate in combined cycle mode when load is down). Solar and Batteries cannot feasibly deliver consistent 200 MW (note the Project is 190 MW however the 200MW scenario is described here for ease of calculation) load at 99.9% reliability without the use of substantial amount of land. For a 200 MW project, with firm reliability at 99.9% in Saint John, a credible engineering estimate is roughly:
Component
Solar PV (DC)
Battery storage
Land for solar
Approximate size
5,000-8,000 MW
15,000-30,000 MWh (3-6 days of full load)
20,000-32,000 acres (~80-130 km²)
The variable nature of the load (i.e. 200 MWs on and off), would be very problematic for any transmission / utility scale grid. For those specific reasons, the selected technical solution is best in class and can meet the specific end use case.
|
Quote:
TRC COMMENT:
While the cooling system will be closed loop, there will be a need to replace water in that system. How and where will the water be disposed of? Are there any quality concerns with the wastewater due to being used in the cooling process upon disposal?
|
Quote:
PROPONENT RESPONSE:
The cooling system is a closed-loop chilled water system. Water loss from the loop is minimal, in the range of 0.1% to 0.5% of total system volume per year, replenished via a small makeup water connection. The loop water contains glycol and chemical additives including corrosion inhibitors and biocides. Under normal operation there is no discharge from this system. In the event of maintenance drain-downs or system flushes, the water will be collected and disposed of by a licensed contractor in accordance with applicable New Brunswick environmental regulations.
|
Quote:
TRC COMMENT:
Municipal tax and assessment impacts
- What is the projected assessed value of the completed project?
- What is the expected annual municipal property tax revenue?
- Are there any expected assessment exemptions, incentives, or appeals?
|
Quote:
PROPONENT RESPONSE:
The assessment will be completed by the Province, and as such, the Proponent is not able to provide this information. The Proponent is not aware of any exemptions, incentives, or appeals currently under consideration regarding municipal tax and assessment.
|
|